Topic:   Water Heater TPR Discharge Piping - 973 visits (1 today, 4 this week)

Shane Pouch
Member
home inspectorhome inspector

Posts: 150
From:Olathe, KS
Registered: Feb 2005

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 23, 2007 12:18 PM     Click Here to See the Profile for Shane Pouch     Edit/Delete Message


Hello to all,

Subject water heater temp/press relief valve discharge piping arrangement.

2006 IRC section P2803.6.1 addresses this.

P2803.6.1.12 Not have valves or tee fittings, is pretty obvious.

But, could P2803.6.1.4 Serve a single relief device and shall not connect to piping serving any other relief device or equipment, also apply? Could the overflow pan be considered "equipment"? Or is this paragraph referring to relief devices or equipment only?

Thanks!

------------------
Shane in KC
"Deal Killer"? Nope...just an ASP (assisted suicide provider)!

vvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvvv
One guarantee about the truth - it comes out the same way every time.

===================================

Books-Reports-Scheduling-Tools

Tim Moreira
Member
home inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspector

Posts: 824
From:New Port Richey, Florida
Registered: Jan 2006

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 23, 2007 01:23 PM     Click Here to See the Profile for Tim Moreira   Click Here to Email Tim Moreira     Edit/Delete Message


Nice attempt at saving about 1 foot of copper.

IMHO, they should be piped separately.

------------------
Tim Moreira
Suncoast Home Inspections
Suncoasthomeinspections@yahoo.com

===================================

Books-Reports-Scheduling-Tools

Thom Walker
Member
home inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspector

Posts: 97
From:Corpus Christi, Texas
Registered: Jul 2001

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 23, 2007 04:42 PM     Click Here to See the Profile for Thom Walker   Click Here to Email Thom Walker     Edit/Delete Message


Look at it this way, Shane. Water takes the path of least resistance. Additionally, the discharge from the TPR will be under pressure. It will add water to the pan.

------------------
when we badly want a thing, we go to hunting for good and righteous reasons for it; we give it that fine name to comfort our consciences, whereas we privately know we are only hunting for plausible ones.

Mark Twain

===================================

Books-Reports-Scheduling-Tools

Jerry McCarthy
Member
home inspector
home inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspector

Posts: 1499
From:San Mateo, CA
Registered: Jan 2001

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 23, 2007 07:03 PM     Click Here to See the Profile for Jerry McCarthy   Click Here to Email Jerry McCarthy     Edit/Delete Message


Nice try!

------------------
Jerry McCarthy
San Mateo, CA

===================================

Books-Reports-Scheduling-Tools

Jerry Peck
Member
home inspector
home inspector
home inspector
home inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspector

Posts: 11902
From:Ormond Beach, Florida
Registered: Feb 2003

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 23, 2007 10:30 PM     Click Here to See the Profile for Jerry Peck   Click Here to Email Jerry Peck     Edit/Delete Message


Water takes ALL available paths, not just the path of least resistance.

Someone went to a lot more work then if they had just run them separately.

What a waste of time.

------------------
Jerry Peck
Ormond Beach
(i.e., Daytona Beach area)

===================================

Books-Reports-Scheduling-Tools

Shane Pouch
Member
home inspectorhome inspector

Posts: 150
From:Olathe, KS
Registered: Feb 2005

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 24, 2007 09:30 AM     Click Here to See the Profile for Shane Pouch     Edit/Delete Message


Come on everybody, back on point. I'm trying to figure out the intent of P2803.6.1.4.

Can the pan (overflow drainage "equipment"?) be considered "equipment"?

Terre G
Member
home inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspector

Posts: 119
From:Astoria Oregon
Registered: Aug 2006

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 24, 2007 01:48 PM     Click Here to See the Profile for Terre G   Click Here to Email Terre G     Edit/Delete Message


Shane,
Good questions! Thanks for posting the picture, Shane.
I don't view the overflow pan as being "EQUIPMENT" in the sense you are asking. However, the WH is equipment. I understand "equipment" as being comprised of parts and components, to form a function that has a mechanical or electrical function. This is supported by the definition for equipment component found in IBC chapter 2:

quote:
"Component, equipment." A mechanical or electrical component or element that is part of a mechanical and/or electrical system within or without a building system.

So to answer your original questions:
"Could the overflow pan be considered "equipment"? NO.
"Or is this paragraph referring to relief devices or equipment only? YES.

The incorrect installation pictured with the PT discharge pipe "Tee'ing" into the overflow pan discharge pipe violates code section P2803.6.1-#12. And it violates TABLE P3005.1 FITTINGS FOR CHANGE IN DIRECTION


A friend in the Building Codes,

Terre Gift
Buidling Official
Astoria & Warrenton, Oregon

,

Jerry McCarthy
Member
home inspector
home inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspector

Posts: 1499
From:San Mateo, CA
Registered: Jan 2001

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 25, 2007 10:12 AM     Click Here to See the Profile for Jerry McCarthy   Click Here to Email Jerry McCarthy     Edit/Delete Message


Shane, note #12 (highlighted)

2006 IRC - P2803.6.1 Water Heaters - Requirements for discharge pipe:
The discharge piping serving a pressure-relief valve, temperature relief valve or combination valve shall:
1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same room as the water heater.
3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor through an air gap located in a conditioned area.
6. Discharge in a manner that does not cause personal injury or structural damage.
7. Discharge to a termination point that is readily observable by the building occupants.
8. Not be trapped.
9. Be installed to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above the floor or waste receptor.
11. Not have a threaded connection at the end of the piping.
12. Not have valves or tee fittings.
13. Be constructed of those materials listed in Section P2904.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.

------------------
Jerry McCarthy
San Mateo, CA

===================================

Books-Reports-Scheduling-Tools

Jerry Peck
Member
home inspector
home inspector
home inspector
home inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspectorhome inspector

Posts: 11902
From:Ormond Beach, Florida
Registered: Feb 2003

Sponsors keep
InspectionNews.com FREE.
Have you clicked on a
banner ad today?

If you don't click,
who will?

home inspection posted March 25, 2007 03:17 PM     Click Here to See the Profile for Jerry Peck   Click Here to Email Jerry Peck     Edit/Delete Message


Jerry M.,

For the purposes of another thread, I will change the bold highlighting around.

2006 IRC - P2803.6.1 Water Heaters - Requirements for discharge pipe:
The discharge piping serving a pressure-relief valve, temperature relief valve or combination valve shall:
1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same room as the water heater.
3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor through an air gap located in a conditioned area.
6. Discharge in a manner that does not cause personal injury or structural damage.
7. Discharge to a termination point that is readily observable by the building occupants.
8. Not be trapped.
9. Be installed to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above the floor or waste receptor.
11. Not have a threaded connection at the end of the piping.
12. Not have valves or tee fittings.
13. Be constructed of those materials listed in Section P2904.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.

Now, how to you accomplish *all* of those and install a water heater in an attic?

------------------
Jerry Peck
Ormond Beach
(i.e., Daytona Beach area)

===================================

Books-Reports-Scheduling-Tools

times are PT (US Pacific Time)

next newest topic | next oldest topic


Administrative Options: Close Topic | Archive/Move | Delete Topic
Post New Topic  Post A Reply Track This Topic via Email
Hop to:

Contact Us | InspectionNews.com

Powered by Infopop 2000
Ultimate Bulletin Board 5.45c

FREE: CLICK HERE and get on board with over 3,575 inspectors and receive a subscription to the InspectionNews.com Information Digest

Training and Inspection Education (Click Here)
"If the class or conference isn't listed here, it probably doesn't exist!"


All Rights Reserved. Hann Tech Marketing Link / InspectionNews.com - No part of InspectionNews.com may be reproduced in any way, or by any means, without the prior written permission of InspectionNews.com. Use of any index or listing Software for the purpose of constructing a mailing list, creating promotional materials or producing a printed or electronic catalog of any kind is expressly forbidden without the prior written permission of InspectionNews.com - All text, graphics and design on InspectionNews.com is copyright by Hann Tech Marketing Links. InspectionNews.com
"Everything an Inspector Needs to Know"
Copyright 2005
Webmaster@InspectionNews.com
HomeInspectorLocator.com
AccessMyReport.com
CostOfBusiness.com
InspectionNews.com
HannTech.com